Remove tankless HW from boiler?

Reply from: salty@dog . com
Date: 11 May 2008, 15:04
Remove tankless HW from boiler?

There is a boiler in one wing of a home I own that has a tankless water heater.
This wing of the house is closed off and not occupied. I only run the boiler
enough to keep pipes from freezing in winter. I would like to disconnect the
domestic hot water since it sometimes makes the boiler run even though there is
no use for domestic HW in that part of the house. Can I simply cap off the cold
water supply to the exchanger, drain it, and forget about it, or do I need to
remove the coil?



Reply from: RBM
Date: 11 May 2008, 15:37
Re: Remove tankless HW from boiler?


<salty@dog . com > wrote in message
news:8erd24lbg8pfmhmhg9hfragv6e1ipees6f@4ax . com ...
> There is a boiler in one wing of a home I own that has a tankless water
> heater.
> This wing of the house is closed off and not occupied. I only run the
> boiler
> enough to keep pipes from freezing in winter. I would like to disconnect
> the
> domestic hot water since it sometimes makes the boiler run even though
> there is
> no use for domestic HW in that part of the house. Can I simply cap off the
> cold
> water supply to the exchanger, drain it, and forget about it, or do I need
> to
> remove the coil?

You could do any or all of the above, but it won't stop the boiler from
running. The easiest thing to do is shut the power to the boiler when the
heating season is over. The other thing you can do is turn down the aquastat
that controls the domestic hot water. This is sometimes a separate device
piped into the boiler's water jacket, and on newer boilers it's often a
triple aquastat relay, which will have a low temperature cut in and a high
temperature cutout within one box. In either case, just turn down the cut in
control as far as it will go, and the boiler shouldn't fire unless a
thermostat calls for heat
>
>



Reply from: salty@dog . com
Date: 11 May 2008, 15:53
Re: Remove tankless HW from boiler?

On Sun, 11 May 2008 09:37:06 -0400, "RBM" <rbm@noemail . com > wrote:

>
><salty@dog . com > wrote in message
>news:8erd24lbg8pfmhmhg9hfragv6e1ipees6f@4ax . com ...
>> There is a boiler in one wing of a home I own that has a tankless water
>> heater.
>> This wing of the house is closed off and not occupied. I only run the
>> boiler
>> enough to keep pipes from freezing in winter. I would like to disconnect
>> the
>> domestic hot water since it sometimes makes the boiler run even though
>> there is
>> no use for domestic HW in that part of the house. Can I simply cap off the
>> cold
>> water supply to the exchanger, drain it, and forget about it, or do I need
>> to
>> remove the coil?
>
>You could do any or all of the above, but it won't stop the boiler from
>running. The easiest thing to do is shut the power to the boiler when the
>heating season is over. The other thing you can do is turn down the aquastat
>that controls the domestic hot water. This is sometimes a separate device
>piped into the boiler's water jacket, and on newer boilers it's often a
>triple aquastat relay, which will have a low temperature cut in and a high
>temperature cutout within one box. In either case, just turn down the cut in
>control as far as it will go, and the boiler shouldn't fire unless a
>thermostat calls for heat
>>
>>
>

Thanks. Are you saying that turning that control down all the way won't affect
the boiler functions of heating of the house? That almost seems too easy. I
thought that control would affect the water temp to the baseboard heating
circuit as well.

I do shut down the boiler as soon as danger of a hard freeze is over. All the
upper floor's domestic water plumbing and baseboards are empty, so I only need
to heat the basement slightly to avoid damage to the foundation. I'm just trying
to save as much oil out there as possible, and don't want to use any oil for
heating domestic hot water that nobody needs.





Reply from: RBM
Date: 11 May 2008, 16:15
Re: Remove tankless HW from boiler?


<salty@dog . com > wrote in message
news:s7ud24hu87fvuj71mosqa722mb2emv859h@4ax . com ...
> On Sun, 11 May 2008 09:37:06 -0400, "RBM" <rbm@noemail . com > wrote:
>
>>
>><salty@dog . com > wrote in message
>>news:8erd24lbg8pfmhmhg9hfragv6e1ipees6f@4ax . com ...
>>> There is a boiler in one wing of a home I own that has a tankless water
>>> heater.
>>> This wing of the house is closed off and not occupied. I only run the
>>> boiler
>>> enough to keep pipes from freezing in winter. I would like to disconnect
>>> the
>>> domestic hot water since it sometimes makes the boiler run even though
>>> there is
>>> no use for domestic HW in that part of the house. Can I simply cap off
>>> the
>>> cold
>>> water supply to the exchanger, drain it, and forget about it, or do I
>>> need
>>> to
>>> remove the coil?
>>
>>You could do any or all of the above, but it won't stop the boiler from
>>running. The easiest thing to do is shut the power to the boiler when the
>>heating season is over. The other thing you can do is turn down the
>>aquastat
>>that controls the domestic hot water. This is sometimes a separate device
>>piped into the boiler's water jacket, and on newer boilers it's often a
>>triple aquastat relay, which will have a low temperature cut in and a high
>>temperature cutout within one box. In either case, just turn down the cut
>>in
>>control as far as it will go, and the boiler shouldn't fire unless a
>>thermostat calls for heat
>>>
>>>
>>
>
> Thanks. Are you saying that turning that control down all the way won't
> affect
> the boiler functions of heating of the house? That almost seems too easy.
> I
> thought that control would affect the water temp to the baseboard heating
> circuit as well.
>
> I do shut down the boiler as soon as danger of a hard freeze is over. All
> the
> upper floor's domestic water plumbing and baseboards are empty, so I only
> need
> to heat the basement slightly to avoid damage to the foundation. I'm just
> trying
> to save as much oil out there as possible, and don't want to use any oil
> for
> heating domestic hot water that nobody needs.

Without knowing the controls you have on the boiler, I can't say for
certain, but a typical modern boiler equipped with domestic coil, will have
a triple aquastat relay, and the low temperature cut in is only to maintain
tank temperature for the coil. The heating thermostat(s) will shunt the "T
T" terminals in the relay and fire the boiler overriding the low temp cut
in, and stay fired until the boiler reaches the high limit, or the zone
calling for heat is satisfied
>
>
>
>



Reply from: salty@dog . com
Date: 11 May 2008, 16:25
Re: Remove tankless HW from boiler?

On Sun, 11 May 2008 10:15:18 -0400, "RBM" <rbm@noemail . com > wrote:

>
><salty@dog . com > wrote in message
>news:s7ud24hu87fvuj71mosqa722mb2emv859h@4ax . com ...
>> On Sun, 11 May 2008 09:37:06 -0400, "RBM" <rbm@noemail . com > wrote:
>>
>>>
>>><salty@dog . com > wrote in message
>>>news:8erd24lbg8pfmhmhg9hfragv6e1ipees6f@4ax . com ...
>>>> There is a boiler in one wing of a home I own that has a tankless water
>>>> heater.
>>>> This wing of the house is closed off and not occupied. I only run the
>>>> boiler
>>>> enough to keep pipes from freezing in winter. I would like to disconnect
>>>> the
>>>> domestic hot water since it sometimes makes the boiler run even though
>>>> there is
>>>> no use for domestic HW in that part of the house. Can I simply cap off
>>>> the
>>>> cold
>>>> water supply to the exchanger, drain it, and forget about it, or do I
>>>> need
>>>> to
>>>> remove the coil?
>>>
>>>You could do any or all of the above, but it won't stop the boiler from
>>>running. The easiest thing to do is shut the power to the boiler when the
>>>heating season is over. The other thing you can do is turn down the
>>>aquastat
>>>that controls the domestic hot water. This is sometimes a separate device
>>>piped into the boiler's water jacket, and on newer boilers it's often a
>>>triple aquastat relay, which will have a low temperature cut in and a high
>>>temperature cutout within one box. In either case, just turn down the cut
>>>in
>>>control as far as it will go, and the boiler shouldn't fire unless a
>>>thermostat calls for heat
>>>>
>>>>
>>>
>>
>> Thanks. Are you saying that turning that control down all the way won't
>> affect
>> the boiler functions of heating of the house? That almost seems too easy.
>> I
>> thought that control would affect the water temp to the baseboard heating
>> circuit as well.
>>
>> I do shut down the boiler as soon as danger of a hard freeze is over. All
>> the
>> upper floor's domestic water plumbing and baseboards are empty, so I only
>> need
>> to heat the basement slightly to avoid damage to the foundation. I'm just
>> trying
>> to save as much oil out there as possible, and don't want to use any oil
>> for
>> heating domestic hot water that nobody needs.
>
>Without knowing the controls you have on the boiler, I can't say for
>certain, but a typical modern boiler equipped with domestic coil, will have
>a triple aquastat relay, and the low temperature cut in is only to maintain
>tank temperature for the coil. The heating thermostat(s) will shunt the "T
>T" terminals in the relay and fire the boiler overriding the low temp cut
>in, and stay fired until the boiler reaches the high limit, or the zone
>calling for heat is satisfied
>>

Thanks very much. The boiler is only a year old, so I imagine the controls are
what you are describing. To be safe, I'll try changing the settings, and wait
around to make sure everyting is okay before walking away from it.



Reply from: RBM
Date: 11 May 2008, 16:39
Re: Remove tankless HW from boiler?


<salty@dog . com > wrote in message
news:1a0e249ts98s4ffcaqmthk919pfn8soabc@4ax . com ...
> On Sun, 11 May 2008 10:15:18 -0400, "RBM" <rbm@noemail . com > wrote:
>
>>
>><salty@dog . com > wrote in message
>>news:s7ud24hu87fvuj71mosqa722mb2emv859h@4ax . com ...
>>> On Sun, 11 May 2008 09:37:06 -0400, "RBM" <rbm@noemail . com > wrote:
>>>
>>>>
>>>><salty@dog . com > wrote in message
>>>>news:8erd24lbg8pfmhmhg9hfragv6e1ipees6f@4ax . com ...
>>>>> There is a boiler in one wing of a home I own that has a tankless
>>>>> water
>>>>> heater.
>>>>> This wing of the house is closed off and not occupied. I only run the
>>>>> boiler
>>>>> enough to keep pipes from freezing in winter. I would like to
>>>>> disconnect
>>>>> the
>>>>> domestic hot water since it sometimes makes the boiler run even though
>>>>> there is
>>>>> no use for domestic HW in that part of the house. Can I simply cap off
>>>>> the
>>>>> cold
>>>>> water supply to the exchanger, drain it, and forget about it, or do I
>>>>> need
>>>>> to
>>>>> remove the coil?
>>>>
>>>>You could do any or all of the above, but it won't stop the boiler from
>>>>running. The easiest thing to do is shut the power to the boiler when
>>>>the
>>>>heating season is over. The other thing you can do is turn down the
>>>>aquastat
>>>>that controls the domestic hot water. This is sometimes a separate
>>>>device
>>>>piped into the boiler's water jacket, and on newer boilers it's often a
>>>>triple aquastat relay, which will have a low temperature cut in and a
>>>>high
>>>>temperature cutout within one box. In either case, just turn down the
>>>>cut
>>>>in
>>>>control as far as it will go, and the boiler shouldn't fire unless a
>>>>thermostat calls for heat
>>>>>
>>>>>
>>>>
>>>
>>> Thanks. Are you saying that turning that control down all the way won't
>>> affect
>>> the boiler functions of heating of the house? That almost seems too
>>> easy.
>>> I
>>> thought that control would affect the water temp to the baseboard
>>> heating
>>> circuit as well.
>>>
>>> I do shut down the boiler as soon as danger of a hard freeze is over.
>>> All
>>> the
>>> upper floor's domestic water plumbing and baseboards are empty, so I
>>> only
>>> need
>>> to heat the basement slightly to avoid damage to the foundation. I'm
>>> just
>>> trying
>>> to save as much oil out there as possible, and don't want to use any oil
>>> for
>>> heating domestic hot water that nobody needs.
>>
>>Without knowing the controls you have on the boiler, I can't say for
>>certain, but a typical modern boiler equipped with domestic coil, will
>>have
>>a triple aquastat relay, and the low temperature cut in is only to
>>maintain
>>tank temperature for the coil. The heating thermostat(s) will shunt the "T
>>T" terminals in the relay and fire the boiler overriding the low temp cut
>>in, and stay fired until the boiler reaches the high limit, or the zone
>>calling for heat is satisfied
>>>
>
> Thanks very much. The boiler is only a year old, so I imagine the controls
> are
> what you are describing. To be safe, I'll try changing the settings, and
> wait
> around to make sure everyting is okay before walking away from it.

All you have to do is turn the low temp cut in all the way down, then turn a
heating thermostat up and the boiler should fire, unless the tank
temperature is already at the limit, in which case it'll fire after some hot
water circulates, dropping it's temperature
>
>



Reply from: hallerb@aol . com
Date: 11 May 2008, 17:18
Re: Remove tankless HW from boiler?

so you have a one year old boiler heating just barely to keep above
freezing a unused space??

i would ask a heating contractor for the option of using the primary
boiler to heat the unused space, thru a zone control.

this woulds shut down the second boiler entirely and may well cost
less.

it could be plumbed by changing some valves to put the secondary
boiler back on line someday.

plus theres no maintence on a unused boiler